This guide shares the detailed procedure for Calibration of HART based Control Valve Positioner.
Calibration of Valve Positioner
-
To prepare the positioner for fail-open operation, slide the “AIR TO” switch to the “CLOSE” position.
-
For small actuators such as the 120cm2, it’s advisable to restrict the output air volume to approximately 50%.
-
Begin the calibration process by entering configuration mode. Using the rotary push button, turn it until parameter 3 is shown, and push the button. Turn again until the display shows “Yes”, and push to accept the change.
-
Parameter 4 indicates the pin position and is set to 35.
-
Parameter 5 sets our travel, and is kept at 15mm.
-
Parameter 6 is changed to nominal to use our 15mm stroke rather than the valve maximum.
-
The final parameter to set is 7, this is our operating direction and is set to increasing-decreasing for standard fail-open operation.
-
Now, go back to parameter zero and press the recessed initialization button to begin the auto calibration process.
-
This process can take a few minutes while the positioner adapts itself to this specific valve and it’s operating characteristics. It is important not to disturb or interrupt this process until it’s finished.
-
Once the calibration is completed, the display will briefly show “Tune”, and then revert to the position specified by the control signal.
-
To confirm correct operation, cycle through various set-points and ensure the valve responds accurately.
-
The positioner is now calibrated and ready for operation.