Dear Guys ,
Could you please help me to set up one Emerson3411P temperature transmitter FF type.
It is a brand new factory configured device, with PT100 Dual Sensor.
Thing is that before installing in the field our QC need to verify the instrument.
So when I am connecting and power up my 475 shows the device tag and LAS but I can not enter in to the device parameters.
So please advice me to see the parameters, I don’t want to change any configuration settings.
Just I will put in amatek and I need to see the temp in 475 as well in Transmitter Display.
Please help me to to the same.
.
John
2
You need FF barrier also which are installed in field junction box.
-
Get one FF junction box to workshop
-
Connect FF Transmitter to Junction Box
-
Connect 18 to 24 V DC power to junction box
-
Then connect HART
Thats it.
1 Like
Ok Noted John. Thank you very much for your information. . But currently I FF JB not available…!!
So is there is any other options .
The 475 prompt when connecting its on temporary address and change in to a different address.
If I Change the same it will affect when connect to DCS ??
these all are my concerns.
Could you please clarify these points.
John
4
You can change the address as per need.
Not an issue.
If need, again you can assign the old address.
1 Like
Ok thanks man …thank you very much.