This can be typically achieved by two ways:
By connecting o/p of one I/P converter to two positioners adjusted suitably for split range operation of control valves.
Taking two AO from DCS/PLC.
Split range to be defined in DCS.
Both I/P converters and positioners to be calibrated with input as 4to20 ma dc and 3to15 psi respectively.