Saudi Aramco Instrument Questions and Answers
Saudi Aramco Instrument Questions and Answers for your interview preparation.
1. What are the parts of coaxial cables?
  • Center Core
  • Dielectric Insulator
  • Metallic Shield
  • Plastic Jacket
2. What is Junction Box?
An earthed enclosure within which wires or cables can be safely connected
3. What are the Kinds of Metering Instrument?
  • Conventional electronic and pneumatic transmitter
  • Transducers
  • Indicators
  • Pressure Gage
  • Thermocouples
  • Resistance Temperature detectors
  • Level Transmitter
  • Instruments air line pressure gage
  • Turbine positive displacement and magnetic flow meters
  • Pilot Tube annular flow meters
  • Temperature gage
4. What are the task in performing instrument loop checking?
  • Conducted as per cable package and markings, Tagging and Wire color coding. Testing to be conducted or using test equipment or hand tools continuity test and referenced loop package documents
  • Considering to identify the Instruments loop (either Closed Loop or Open Loop)
  • Obtain Documents pertaining to the process loop in order to understand All devices and their intended functions
  • Inspect the loop components through visual observation in order to ensure that the components are correctly installed
  • The prepared approved Instrument loop package or folder shall be always implemented
5. What is instrumentation?
It is a branch of science which deals with measurement and control of process variables such as pressure, flow, temperature, level and etc.
6. What are the kinds of pressure measurement?
  • Pressure Gauges
  • Draft Gauges
  • Pressure Switches
  • Pressure Transmitters
  • Deferential Pressure Instruments
7. What are the Kinds of Smoke Detector?
  • Air Sampling type detector
  • Automatic fire detector
  • Automatic Fire Extinguishing or suppression system operation detector
  • Combination detector
  • Electrical conductivity heat detector
  • Fire-Gas Detector
  • Fixed temperature detector
  • Flame detector
  • Heat detector
  • Line-type detector
  • Other Fire detectors
  • Pneumatic rate-ofrise tubing heat detector
  • Projected beam-type detector
  • Radiant sensing fire detector
  • Rate compensation detector
  • Rate offrise detector
  • Smoke detector
  • Spark/Ember Detector
8. What are the Types of Switches?
  • Lever actuator limit switch
  • Proximity Switch
  • Speed switch
  • Pressure switch
  • Temperature switch
  • Liquid level switch
  • Liquid level flow switch
  • Nuclear level switch
  • Toggle switch
9. What are the Kinds of Alarm Control Unit?
  • Fire Alarm Control Unit (Panel)
  • Intermediate Fire Alarm Fire Supervisory control Unit
  • Master Control Unit (MCU Panel)
  • Protected Premises (Local Control Unit Panel)
10. What is the Saudi Aramco Instrument Signal Pair wire color coding?
  • P – Black
  • N – White
11. What is the Saudi Aramco Instrument Signal Triad wire color coding?
  • P1 – Black
  • P2 – Red
  • N – White
12. What are Instrument Loop-package Documents Contents?
  • Applicable design documents
  • Procurement documents
  • Manufacturer’s documentation needed to test and verify loop operation
  • Completed quality control RFI checklists and test reports from receiving, installation, and calibration
13. What Items we should to check for Instrument Stand / Supports?
  • Fabrication of Stand as per drawing
  • Deburred , Primed and Painted
  • Instrument location as per IPL Drawing
  • Access is unobstructed and clear for maintenance
  • Stand Grounded
  • Stand and Support Secure
14. What Items we should to check for Instrument Device Installation?
  • Instrument Calibrated prior to installation and documentation checked
  • Instrument mounted in accordance with hook up drawing
  • Check instrument is correct in accordance with ISS / P & ID
  • Instrument securely installed on stand
  • Elevation correct relative to process tapping
  • Sunshade installed
15. What Items we should to check for Instrument Impulse Tubing?
  • Material used according to specification
  • Steam tracing and insulation as per hook up
  • Seal fitting installed and Filled
  • Isolation and equalization valves / manifold installed
  • Vent and drain / manifold installed
  • Tubing slope Checked
  • Verify Tubing connection to HP & LP sides
  • Leak Test done
  • Pressure Test of impulse tubing
16. What Items we should to check for Instrument Cabling / Signal / Conduit?
  • Check electrical installation with respect to conduits, glands, seals, are correct
  • Core and cable tagging are meggered and checked
  • Check connection terminations with instrument for tightness
  • Instrument installation pressure tested as required
17. What kinds of materials being used for impulse tubing pressure leak testing?
  • Nitrogen
  • Water
18. What are the test procedures of Pressure Transmitter?
The process connection shall be connected to a dead weight tester Budenberg (Range 1-1200 bar g) or equivalent
  • The output signal shall be connected to an electronic test meter or precision manometer as applicable
  • Align equipment at zero
  • Apply actuating pressure to full range and lock-in signal pressure- check system for leaks
  • Reset to zero
  • Apply actuating pressure of 25,50,75 and 100% of range-record readings
  • Reduce actuating pressure of 75,50,25 and 0 % of range-record readings
  • When necessary, adjustments according to the manufacturer’s instructions shall be made until the quoted accuracy is obtained
  • Apply 110% signal as check for hysteresis
  • Transmitters with indicating scales shall have the indicator calibrated during the above tests and the transmitters color coded
19. What are the specific contents of Material Requisition (MR) in Saudi Aramco?
  • SCOPE OF SUPPLY
  • REVIEW CHECKLIST
  • EQUIPMENT / MATERIAL DESCRIPTION
  • QA/QC REQUIREMENTS
  • GENERAL REQUIREMENTS
  • VENDOR DOCUMENTATION REQUIREMENTS
  • SPARE PARTS DATA PACKAGE
  • LIST OF ATTACHMENTS
20. In Area Classification what are the difference between Class 1 Zone 0, Class 1 Zone 1 & Class 1 Zone 2 Location?
Class 1 Zone 0
In which ignitable concentrations of flammable gases or vapors are present Continuously and in which ignitable concentrations of flammable gases or vapors are present for long periods of time.
Class 1 Zone 1
In which ignitable concentrations of flammable gases or vapors are likely to exist under normal operating conditions or vapors may exist frequently because of repair or maintenance operations or because of leakage and in which equipment is operated or processes are carried on, of such a nature that equipment breakdown or faulty operations could result in the release of ignitable concentrations of flammable gases or vapors and also cause simultaneous failure of electrical equipment in a mode to cause the electrical equipment to become a source of ignition.
Class 1 Zone 2
in which ignitable concentrations of flammable gases or vapors are not likely to occur in normal operation and if they do occur they will exist only for a short period or in which volatile flammable liquids, flammable gases, or flammable vapors are handled, processed, or used, but in which the liquids, gases, or vapors normally are confined within closed containers of closed systems from which they can escape, only as a result of accidental rupture or breakdown of the container system and in which ignitable concentrations of flammable gases or vapors normally are prevented by positive mechanical ventilation, but which may become hazardous as a result of failure or abnormal operation of the ventilation equipment.