Shutdown valves will typically be actuated (but occasionally motor driven) ball valves located on the perimeter of the isolated section.
The isolation of sections of plant will typically be an engineering judgement based on:
The purpose for the isolation; either maintenance/operation or shutdown
The design condition of the section, particularly pressure
The nature of the fluid in the section, e.g. flammability, toxicity etc
Isolation of a section for shutdown purpose will always consist of a single, actuated valves on the perimeter, which will respond to a shutdown signal(s) from ESD systems. Single shutdown valves are normally sufficient for the event initiating the shutdown and associated risk
Shutdown valve is a block valve that is actuated through the PSD and ESD system and used to isolate sections of plant
These type of valves usually have 3 signals output and 8 input status that are shown in the control room,
Input:
- Group Reset
- keyswitch SDV
- close command
- Logic command not trip
- open limit sw
- close limit sw (not close)
- Timer SP
Output:
- Valve Command “Open”
- Logic status “Trip”
- Discrepancy alarm
The logic are:
If the logic command trip, logic status trip will be activated
The valve cannot be opened until SDV switch, close command and Logic command trip deactivated and Group reset command becomes active.
If valve is in open condition but limit switch closed active, Discrepancy alarm shall be activated
If valve is in close condition but limit switch open active, Discrepancy alarm shall be activated